      1st, be sure you post a fishing report in the forums, then ask to join after you post a fishing report in your area forum. The Private Fishing Report Clubs are where folks can share private fishing information with club members who have proven they know what's going on. Fishing Report Clubs Link also in Menu above. Apply to become a member today, while it's still easy. 
  • RECEIVE THE GIFTS MEMBERS SHARE WITH YOU HERE...THEN...CREATE SOMETHING TO ENCHANT OTHERS THAT YOU WANT TO SHARE

    You know what we all love...

    When you enchant people, you fill them with delight and yourself in return. Have Fun!!!

  • 0
Sign in to follow this  
Squid

Atwood Furnace Not Heating

Question

Squid

My season is getting off on a bad start. My fishhouse on wheels also serves as a bunkhouse for deer season. So, in the process of giving it a checkout Friday morning my heater didn't heat. I thought it was perhaps a bad regulator but nixed checking it out until after the weekend.

So, after checking it out yesterday I'm at a loss as to what is wrong with it. Everything seems to be working but it appears to not be getting any propane. The tank is full and I disconnected the regulator to see if gas is getting throught the valve, which it was. The thermostat turns the fan on and you can hear the ignitor but no flame. The unit is an Atwood Model 7916-II. The installation manual has a diagnostic chart but the LED indication seems to be normal (blinks on green at @ 8 sec intervals).

Has anyone else had any problems with this? I know this has been a fairly common unit to be installed in fishhouses and I'm hoping someone else out there has had a similar problem.

Share this post


Link to post
Share on other sites

19 answers to this question

Recommended Posts

  • 0
PierBridge

Bad thermocouple or a Cobweb in the gas line of the heater.

Share this post


Link to post
Share on other sites
  • 0
backlash 1

Do you have a gas stove top or lantern on the same line that is working? If the other things are not working, then I would say froze up regulator. If the regulator is upside down, it can let rain water get in the vent, causing it to freeze up every time it gets cold out. Been there, done that. Good luck.

Share this post


Link to post
Share on other sites
  • 0
Surface Tension

Is the battery at a full charge?

Share this post


Link to post
Share on other sites
  • 0
bbqhead

very good point,

if you have a low battery the fan will come on

but it will not open the gas valve on the furnace.

its like below 11 volts the valve will not open,

bbqhead

Share this post


Link to post
Share on other sites
  • 0
Squid

The battery was fully charged, I even swapped it with the one for the lights but it didn't change a thing. It's like the gas valve is stuck shut. I see there is a screwdriver slot on the front of the valve but I haven't touched it because I can't find any mention of it in the installation manual. Is it possible for that to get stuck? The unit worked the last time it was used at the end of the last ice season. The hose was capped at the regulator end, so I don't believe there's a blockage in the line either.

Share this post


Link to post
Share on other sites
  • 0
bbqhead

where is this furnace located?

citywise. so many things it could be...

you can call me at 651-7175466

bbqhead

rv tech

Share this post


Link to post
Share on other sites
  • 0
fishinalot

You may have dirt or dust on the electronic circiut board.

Share this post


Link to post
Share on other sites
  • 0
Dogzlife000

The sail switch is likely dirty. It's a small safety switch located near the blower that when closed, due to the fan air flow, allows the main gas valve to open. It's a somewhat delicate mechanical switch so you could have some crud or something jamming it.

This switch is located near the blower motor. If you look on the right side of the furnace, the two wires that run along the blower duct tube go to the sail switch. Very easy to get at once the furnace is removed.

Share this post


Link to post
Share on other sites
  • 0
Biggerfish

How old is this heater? I have the same in mine. I hope its not a sign of what is to come. Please post how you fixed yours. Thanks in advance.

Share this post


Link to post
Share on other sites
  • 0
kooba

I would say frozen up regulator. This happened to me a couple of years ago. Same problems. I used a blow dryer on the regulator and it solved the probelm. Water got in the little vent and froze. Just make sure the regulator is in the correct position. KOOBA

Share this post


Link to post
Share on other sites
  • 0
pikechaser

if your getting spark and you have gas to the gas valve..id check the burner orifice. possibly clogged with spider webs,,may have to actually remove the orifice to see, depending on the type of orifice may be tough to tell otherwise

Share this post


Link to post
Share on other sites
  • 0
Squid

Haven't really had a chance to look at the suggestions that everyone has come up with until today. When I tried to fire it up today I noticed that once the cover was off it would try to start up, the blower ran for a minute or two and then shut down. It was then I noticed that a red light on the circuit board blinked three times every three seconds. From the installation manual this states this is an ignition lockout fault. Any suggestions? The unit is located in Waconia.

Share this post


Link to post
Share on other sites
  • 0
Dogzlife000

Squid, post your email address and I will send you a service manual. Although it could be another cause, the most likely in your case is a sail switch failure. If the switch doesn't close, the gas valve will not be energized. Could be a limit switch failure, a dirty edge connector on the circuit board, a plugged main orifice, or a couple of other things. Since you mentioned that it is the first time you attempted to fire it up this season, in all likelihood, it's a mechanical and not electrical failure. My 7920P furnace had a sail switch failure due to a mouse nest in the ducting.

Pete

Share this post


Link to post
Share on other sites
  • 0
Squid

Today's the first chance that I've had some time to look into this. The sail switch seems to be working correctly. I was able to remove the blower assembly and found no obstructions to it. With a meter there was continuity with the switch closed. There was continuity across the Limit switch also. After that I swapped out the regulator with no success. The edge connector on the circuit card looked clean and all the connections looked in good conidition also. Having done all of that it's down to the circuit card, thermostat or possibly a defective gas valve. Everyting seems to be working but it just acts like the ignitor doesn't have any juice or the main valve isn't opening up. You can e-mail me at jeffmcleod2@earthlink.net. I'm at whits end on what to do next.

Share this post


Link to post
Share on other sites
  • 0
Dogzlife000

Jeff, I emailed you the service manual.

What I would do next is to attempt to fire up the furnace and check for voltage at the main valve. Once the blower turns on, there is about a 15 second delay caused by the relay to purge the combustion chamber. Then, if the sail switch closed properly, you should have voltage at the main valve. If no voltage at the main valve, check for voltage at the limit switch (current runs from the sail switch, through the limit switch, and to the main valve). Easy to check and will help to isolate the issue.

Pete

Share this post


Link to post
Share on other sites
  • 0
Finn-Hunk

Take the spring clips that hook up to the battery off. Hook up the bazttery direct with a eyelet or a direct terminal, so that is makes good contact and give this a tryl I had the some problem and just tried mine this way and all I had to do was give the thermostat a slight tap and away the furnace went. The spring clips do not make a good connection.

Share this post


Link to post
Share on other sites
  • 0
Squid

Hey folks, the problem has been solved. It was pretty much a mystery to be until I got some help and encourage from DogzLife000. When I took the burner head out there was the mystery. What should have been a empty combustion chamber had been turned into a nesting site. Over the course of the summer some unknown birds had entered through the exhaust outlet and had built one heck of a nest, complete with grass and pine needles. What a mess. The needles had dried out put some of the pitch had stayed behind. The whole furnace had to be removed and with some elbow grease, a wire brush and a vacuum cleaner it finally got cleaned out. After re-installing it there was sigh of relief when it fired up the first time and cycled just like it supposed to.

The lesson learned here for everyone of you that has this type of furnace is that when you put it away after the season make sure you block off the outlet. There will be some disappointed birds next spring but better it be them than me.

Share this post


Link to post
Share on other sites
  • 0
PierBridge

Glad to hear it....and thanks for keeping us updated.....

Share this post


Link to post
Share on other sites
  • 0
ice_it_06

There must be a pretty good sized open outlet on it I assume.

I have my first Suburban furnace whick looks the same of a Atwood but it has a spring loaded screen cover over both vents which I assume is to prevent what happened to you.

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  



  • Your Responses - Share & Have Fun :)

    • Knowknot
      Great video Curt, for as much of it that I could see. Keep up the good work, and one question, Are there any live emerald shiners around the Baudette area to be had, or just frozen ones?
    • eyeguy 54
      Its a little stiffer than my titanium spring boober and much more sensitive.  I like it  better than the 27 inch ul ticklestick. Only used 3 and 4 mm jigs so far. Thumbs up from me. 
    • Troy Smutka
      2/18/18     Got out on an area lake an hour before sunrise Saturday. Got a bunch of crappies until they slowed about 9 am. Most between 9.5 and 11 inches. Sunfish started biting about sunrise and bit all morning. Half of them were 8 to 8.5 inches. Most of the rest were 7 to 7.5 inches. Kept two meals of fish--released the rest. 1/32 ounce VMC Tungsten Tubbies tipped with a single wax worm or two red Eurolarvae fished just above some weeds in thirteen feet of water caught fish after fish. Lots of good ice on area lakes. Even though walleyes and pike close in just over a week and wheel houses can't stay out unattended soon, still a lot of good ice fishing for panfish to come. Will have plenty of ice for a while, so get out and enjoy the peace and quiet and fast crappie and sunfish action that March will bring. Good luck, and I will see you out there somewhere.
    • IceHawk
      Had a chance to rub shoulders and fish with some of the ice team guys today. Great bunch of guys we had some good laughs and of course discussed plenty about fishing. Even shared a few hotspots. The hands on they give the people that sign up for this event is absolutely amazeing! From hands on to tips on everything to do to make your day on the ice way more productive. From what I witnessed it would be well worth the investment to sign up for one of there events , if you are new to fishing or heck even a seasoned angler.  Fished with one guy from Nebraska said he has done 5 of these events and has enjoyed everyone of them.  Fun day for sure 
    • AlwaysFishing23
      Royce, how’s the sensitivity Is the tip soft like a tickle stick and how’s quality seem? About same price as a tickle stick I see may have to try one for next season. If It passes with flying colors do you it must be good! Tough day for me not much happening went from about 8-29 FOW and just nothing. Found perch in about 19 but even they seemed finicky and would only hit the dead stick. A bit windy on the lake today to!
    • The Chemist
      Yes that would be the one. A friend of mine sent it to me. The guy who got it is a friend of his nephew. 
    • The Chemist
      So that explains the traffic and also the one where they were shooting video of what appeared to be about a drill type auger. Did drive by an ice team truck on the way out also.
    • The Chemist
      The warmer weather has brought alot of people out to the area. We are waiting for the later bite. Most are setup in shallowet water. Haven't marked fish yet but tendto see them at sunset.    Be careful with all the holes being drilled! I found one that was covered back in, got my shin, luckily not my ankle.
    • eyeguy 54
      Started out in 26 feet this morning and had 5 dandy crappies in 15 minutes then it was over. moved a mile and found a few dandy gills in 16 feet. And a couple bass.  Day 2 with the new rods and liking them more. 
    • monstermoose78
      I would fish them trees
  • Share & Have Fun