heater venting problems


Brett Meyer

Question

I have a direct vent heater in my fish house and i have a problem with the venting. It usually runs fine but when a gust of wind comes up, or if it's windy, the flame goes out. It is a radient heater with the exhaust above the intake. If anyone has any sugestions let me know. I spent some money getting this heater fixed and would like to keep using it, but it's not very practical right now.

Link to comment
Share on other sites

14 answers to this question

Recommended Posts

  • 0

Sounds like you may also be spilling flue products into the house. Try to face the vent to the south or extend the vent with an elbow 12 inches above the roof. Use the match test(light a match and blow it out and make sure the smoke goes up the vent) to check for flow.

------------------
Mille Lacs Guide Service
651-271-5459
www.millelacsguideservice.com

Link to comment
Share on other sites

  • 0

The match does go out when I try and light it too. If i put that elbo on there do i just put it on the exhaust, and leave the intake, and will it work good, without trying to rig up some kind of damper on it? just trying to cover everything. I'll have to try that this weekend. That was the one thing i didn't want to do was run a pipe up, but if it works, i might as well.

Link to comment
Share on other sites

  • 0

I have tried facing the house in all different directions but the wind always turns on me and i don't feel like moving my house and re-drilling and all that stuff. I have also made some "beer case" baffles with no luck.

Link to comment
Share on other sites

  • 0
  • 'we have more fun' FishingMN Creators

A pictures worth a thousand words.....
What kind of air supply and vent cap/hood termination do you have? Do you have the owners manual with recommended installation instructions? I take it this is a horizontal setup?

Link to comment
Share on other sites

  • 0

It is a horizontal pipe set up, with the exhaust pipe about 6 inches dierectly above the intake, with a double intake/exhaust cap(?). I will try to get a picture this weekend up, maybe that will help. It is a Saf-Aire made by stuart warner. I got a from a buddy who bought it at an auction, so I am running blind on how it should have been installed. I did it to the best of my knoledge.


[This message has been edited by Brett Meyer (edited 10-03-2003).]

[This message has been edited by Brett Meyer (edited 10-03-2003).]

Link to comment
Share on other sites

  • 0
  • 'we have more fun' FishingMN Creators

Im intersted in seeing the hood/cap. Did it come with the heater?

Link to comment
Share on other sites

  • 0
  • 'we have more fun' FishingMN Creators

Is the regulator original?

Link to comment
Share on other sites

  • 0

I will try and get a picture of it up tomorrow. the regulator is new paid about $130 for it. The guys I got it from said that they don't make that model anymore, and that was the next best thing. other than the flame getting blown out it works fine.

Link to comment
Share on other sites

  • 0
  • 'we have more fun' FishingMN Creators

I cant tell anything from the photos.
The regulator should have cost you around 25 bucks. If the hoods are original my guess would be wrong regulator or it has orifices for natural gas.
I searched around on the net for a manual and parts and got nowhere.
You might try bringing the shack to a furnace guy and have him take a quick look.

Link to comment
Share on other sites

  • 0

yeah it wasn't a regular regulator, it was the carborator thing for the furnace, that's why it was spendy. I talked to a few guys about it and they said i might just be able to extend the exhaust pipe a few inches. If that doesn't work i will bring it over to the heater shop.
Thanks for your help anyways!
I'll let ya know if i get it fixed.

Link to comment
Share on other sites

  • 0

Brett,, a few questions about your heater. does the pilot go out? are you sure its a dedicated direct vent appliance? if it is, then the intake pipe will need to be connected to the appliance as well as the exhaust vent. the vent kit that comes with the heater will have the proper connections. usually its a pipe within a pipe, check out Reznor or Modine heaters for a picture of the direct vent type kits. sometimes the intake pipe is too close to the bottom of the exhaust cap where it goes through the wall on the outside. some manufacturer recommend as much as a 6" clearance between the intake and the bottom of the exhaust cap. this is to insure that exhaust gases aren't recirculated through the burner. if its too close the exhaust can be sucked in when a gust of wind hits. also, there is an over heat safety inside the heater called a klixon make sure that it isn't dropping out the flame. if you had a natural gas heater and you were using propane you would of known it rather immediately. the propane regulator will be set at about 10", the nat gas regulators are set about 3-4". if you lite a match inside and it goes out you either have co or no air. if the house is so tite and the heater goes out, your venting is improper and you're burning the air in the house, or you're dumping carbon mon. inside from improper venting. also, the heater may not be sidewall ventable and it may need to go through the roof. Don't alter the appliance write to the manufacturer and find out what they say.

Link to comment
Share on other sites

  • 0

This heater came out of a house, and the new carb is for propane, and i beleive it says propane fuel on the heater. The match does go out when i try lighting it, it's sucking air into the heater fast enough to blow out the match. I have had my CO detector go off a couple times, had to be from the heater (not my cook stove). I have the original vent cap for it on. The only thing that i did to it was cut off the intake, and exhaust pipes about 4-6 inches. I think that is where i went wrong, the pipes are not long enough. plus i think i need to put some kind of a gasket behind the heater to prevent air going thru around the pipes.

I works great when the wind isn't blowing.

I'll try a couple things this weekend if i get a chance, and let ya know.

[This message has been edited by Brett Meyer (edited 10-15-2003).]

Link to comment
Share on other sites

Guest
This topic is now closed to further replies.


  • Your Responses - Share & Have Fun :)

    • ADAS
      don't know what roulette is? Hi. Roulette as I think is a very cool game. Roulette has been played since the nineteenth century and every self-respecting casino, including online casinos, be sure to have it in their assortment https://aolbroadband.in/ .Games for free, which the guys provide on this site, of course, include the most popular varieties of roulette: American, European and French. The online version of roulette is no different from the well-known one from land-based casinos: it features a green table with marked numbers and betting fields, as well as a wheel with numbered cells on which the ball rotates. On this site you can learn more and even play it 
    • andrew2
      In addition to to Feichao, you can also consider the DJI Mini SE. This is also an excellent piece. However, always try to read articles and thorough reviews before buying.
    • andrew2
      Mini drones like Feichao Mini Drone Quadcopter M9 are good to take footage.  
    • FrankOcean
      My grandmother is a very old person, and she has had a real estate company for 20 years now, she has dedicated her whole life to it, so she does not understand much about technology and is looking to modernize her business, she is one of the few real estate companies that They don't have their own application, so I see myself in charge of finding a good software developer for real estate and that type of business. Do you know any professional or company that is dedicated to it?
    • BobT
      Don't forget about IP Lures just west of town about 2 miles on the south side of Co. 82.    I was out on Osakis last week for a couple hours. Picked up two walleyes, one about 13" and the other a fat 14-1/2". Also a couple northerns and a handful of perch.
    • Andre.y
      Of course, you shouldn’t even ask about this, because this is the responsibility of the executor of the order, that is, the employee who will create such an application. I think it will be stated in the contract of employment if there is one and then you don't have to ask for anything.
    • smurfy
      👍 awesome sauce!!!
    • CigarGuy
      Shallow. Got skunked tonight. Just got chased off by the weather. Last evening was the only time the last 4 times out I caught fish. Last even was light drizzle and calm water. Water warmed up about 3-1/2 degrees since the first time out.
    • Kettle
      Got into the cranes, 5 a piece this morning for two of us  
    • Fasterok
      It is very important not only to identify mushrooms by their appearance but also to understand whether it is useful or not, because now there are many poisonous mushrooms, and it is extremely important that no mistakes were made in the selection of such mushrooms. That's why I here https://www.mushrooms.online/mushroom-poisoning/ read a lot of interesting information about poisonous mushrooms and was able to understand more about it. I hope that I was able to help you and was really helpful to learn. 
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Privacy Policy. We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.