      Fishing Minnesota had added a new menu item (see above) called Fishing Report Clubs. It's a way to keep the really good fishing reports coming and being shared only with those who also provide detailed fishing reports. We will only approve new members who request to join if they have already posted a recent fishing report in the area forum, associated with the Fishing Report Club area  you want to join. We are going to limit the number of regular memberships, in the Fishing Report Clubs, to the top 20  members in each Club, to those with the best frequency and quality fishing reports provided in the club and less so in the regular fishing report forum open to all members. The higher quality fishing report reserved for the club of course. If  you want fishing reports  around your area, I would Join Now, some of the clubs are starting to fill fast. Use the Fishing Reports Club link in the Menu above (after you've posted a fishing report in the regular area forum) and request to Join.
  • RECEIVE THE GIFTS MEMBERS SHARE WITH YOU HERE...THEN...CREATE SOMETHING TO ENCHANT OTHERS THAT YOU WANT TO SHARE

    You know what we all love...

    When you enchant people, you fill them with delight and yourself in return. Have Fun!!!

  • 0
Sign in to follow this  
eel pout hunter

LP gas and OPD valve problems

Question

eel pout hunter

hey all, in need of some help again.

Just bought my first ice house (used). It has a heater in it, but I'm putting in a stove as well. Its of the Coleman variety with it's own regulator. (kind made to run off of 1lb tanks, but can be used with a bulk cylinder with an adapter). Here's the problem. Every single time, and I mean every time I turn either on, the OPD valve kicks in.

Here's the set up....tank to a 3 ft hose, to a tee...from one leg of the tee is the heater regulator going to the heater. From the other leg is 8ft of 3/8 copper going to the stove regulator. If I take the tee out, and hook up each device directly to the take, they work fine, however with the tee in place the valve kicks in. Not sure why...there are no leaks in the system....any ideas would be greatly appreciated.

pout

Share this post


Link to post
Share on other sites

11 answers to this question

Recommended Posts

  • 0
federline

Can you try some different OPD equipped tanks to see if it does it with all OPD valves, or just this one? What year was the tank made in? Some of the first OPD valves didn't flow well at all and were touchy like this.

I would also be suspect of your 3 foot length of hose. If you just use the 3 foot length to one or othe other, does it work OK?

Share this post


Link to post
Share on other sites
  • 0
tomfromblaine

Explain what you mean by the opd valve kicks in, my impression was that the opd was a safety device to prevent a over fill/pressure situation. I've heard of opd issues when the outside temp starts to get way down.

Share this post


Link to post
Share on other sites
  • 0
federline

OPD's will kick in in high-flow conditions to prevent things like a ruptured hose from evacuating the entire tank at once. Sometimes, the check-valve kicks in at flow rates that are desired under normal operation.

I've even seen some that, if you turn the wheel on ALL THE WAY, they are much touchier to flow and can check-off. In those cases, don't turn the wheel all the way on.

Share this post


Link to post
Share on other sites
  • 0
eel pout hunter

I haven't tried using either device with a 3ft hose....but when I d/c each device from the tee and run it independantly it runs fine. The problem is whenever I put the tee in...with the tee in place neither device works, not even one at a time.

but this is the interesting part. when I d/c the line to reset the valve, I can here gas coming from the line and not the tank (sort of a back pressure, which would explain why the OPD kicks in)

I'm aware of the 1/4 turn trick, don't work either lol

Do you think putting the tee right at the tank would make a difference?

not sure, I've been playing with this for days.

pout

Share this post


Link to post
Share on other sites
  • 0
eel pout hunter

OK, here's the update.

Disconnect the whole shootin match...heater works fine. The stove however seems to be the thing that triggers the valve.

It worked at one time. Here's the set up....tank, acme nut, adapter (mpt), 10 ft run of copper 3/8, then 2 3/8 elbows, the reducing to 1/4, to bulk tank adapter, then the regulator.

So here's what I'm thinking, the bulk tank adapter is the wrong kind. By going from 3/8 to 1/4 (the adapter is 1/4 by whatever size those 1lb bottles are) there is too much resistance, thus the back pressure triggering the OPD.

I'm going to call Coleman in the AM. Maybe the regular bulk tank adapter don't work with their stove.

pout

Share this post


Link to post
Share on other sites
  • 0
Jeremy airjer W

Eelpout, How old is your tank? There should be a four number date stamp on the collar. Some of the older tanks had a considerably lower flow rate than a typical non OPD tank or a newer OPD tank.

The other possibility is that the Excessive Flow Device check valve is tripping. This is an additional safety device designed to limit the flow of propane in the event of a hose bursting. We run into a few of these that are really sensitive and trip when filling the tanks. All we do is shut of the fill valve and then shut off the valve on the tank. Wait for a light clicking noise and start over. We also have alot of people bringing in there full tanks to be filled because they can't get there grill to light. A quick Q&A and we find out they did things in the wrong order and tripped the EFD.

The OPD "Overflow protection device" is nothing more than a "float" that stops the flow of propane "into" the tank when the tank is at its theoretical 80% full. This float/valve has nothing to do with the flow of propane out of the tank.

Share this post


Link to post
Share on other sites
  • 0
eel pout hunter

Quote:

Eelpout, How old is your tank? There should be a four number date stamp on the collar. Some of the older tanks had a considerably lower flow rate than a typical non OPD tank or a newer OPD tank.

The other possibility is that the Excessive Flow Device check valve is tripping. This is an additional safety device designed to limit the flow of propane in the event of a hose bursting. We run into a few of these that are really sensitive and trip when filling the tanks. All we do is shut of the fill valve and then shut off the valve on the tank. Wait for a light clicking noise and start over. We also have alot of people bringing in there full tanks to be filled because they can't get there grill to light. A quick Q&A and we find out they did things in the wrong order and tripped the EFD.

The OPD "Overflow protection device" is nothing more than a "float" that stops the flow of propane "into" the tank when the tank is at its theoretical 80% full. This float/valve has nothing to do with the flow of propane out of the tank.


Ok, I figured it was the Flow device portion of the tank. I see a couple of 4 digit numbers on is 43-00.

I spoke with the Coleman people today, all they wanted me to do is buy their hose. I'm off to the local gas company today to talk to them and see what their input is.

I'm starting to think that I've got the wrong style of bulk tank adapter, but I'll keep ya posted.

pout

Share this post


Link to post
Share on other sites
  • 0
Jeremy airjer W

Your on the right track!

The date stamp is a 2 digit month followed by a 2 digit year. Examples, 12 00 (december of 2000) or 09 94 (september of 1994)

Share this post


Link to post
Share on other sites
  • 0
eel pout hunter

OK, here's the final update, the good news is, the problem is solved.

The gas company people were a bit of help. They stated that because of the amount of tubing, the excess flow valve kicks in. They taught me how to open and close the valve like six times in a row to 'purge' the lines. This worked fine on just the stove that I took to them.

They also stated that I could use a POL adapter and that would bypass the excess flow valve. I really wanted an acme nut style fitting so that it would be easy to hook up with cold hands. So they sold me a universal adapter. This was an adapter that was sold after all the grill companies switched to acme nuts, and OPD wasn't a standard. It screws into the POL (inner) thread and has a male acme nut on the other end.

This didn't work however. So basically you need to use a straight POL fitting without the acme nut stuff. Fired it all up tonight and it works fine.

Thanks for your help, just thought that I would post this in case anyone runs into the same problems.

pout

Share this post


Link to post
Share on other sites
  • 0
Jeremy airjer W

Well I learned something new. I never realized that an empty hose or purging on empty hose would trip EFD, but it makes perfect sense! Everything that I have used has always had the POL ends so I have never run into a problem with the EFD. I'm starting to think that my idea of switching to the ACME connector might not be a good idea!

Share this post


Link to post
Share on other sites
  • 0
eel pout hunter

Well then I'm glad I posted the update. I have to go into town today and return the universal adapter ($16). I'm gonna talk to them about the acme nut, it must have something to do with the EFD, reason I say this is because with the universal POL adapter, that is supposed to prevent the EFD from kicking in, not sure why is does.

I guess I should try to find a POL fitting that has a plastic knob on it. They used to make such a critter for gas grills.

pout

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  



  • Your Responses - Share & Have Fun :)

    • Head Shot
      Hello: Repairing Coleman Focus 3 / 5 / 10 / and certain model numbers for the focus 15. If your coleman focus heater is in need of a rebuilt burner or other parts I can help. I do supply parts and repair the above heaters including rebuilding burners for the heater. Qestions = give me a shout. Head Shot eklb@mediacombb.net
    • Cliff Wagenbach
      Pat, July is my best time for walleyes in the weeds! I did not cast spinner baits but did pull spinners with 1/2 crawler right along the edges in about 3' to 4' deep water. We were so close to the boat with our lines that we could see our spinners and actually see the walleyes charge out of the weeds and grab our baits! FUN!! Now, thanks to the rustys, those cabbage weed beds are gone. Cliff
    • derbier122x
      That's the plan. I'e gotten checked quite a few times this winter. It's good to see them out. Watched them get a couple guys last Thursday for too many lines, too many and illegal fish and using jawjackers... Sure is good seeing some of our money at work. Silly thing is the officer checked me 1st, then walked 50 yds to the other guys...  can' fix stupid I guess.
    • Pat McGraw
      Thanks Cliff
    • Pat McGraw
      Years back I took my brother-in-law behind Anselmo's (SP?), northwest of Jacobson Point in Head-o-Lakes Bay. I was looking for Muskie along the front of the cabbage. He had no gear so he rigged a small to mid-size in-line spinner bait with a white twister tail. He pulled it across the top of the cabbage beds. I was totally surprised when he caught several walleye. I wouldn't be so surprised if he was fishing in front or down in the weeds but he was basically catching on a surface lure in 3-5' of water in July.
    • Cliff Wagenbach
      Under bite jaw = whitefish! Cliff
    • PRO-V
      Nice. I made my own like that a few years ago but without the usb port. Can run a fan, light, charge phones etc. They are very handy.
    • PRO-V
      Frozen ones work better in my opinion anyway. Haven't bought a live one in 10 years.
    • tcbow
      We made a day trip a couple of Sundays ago. Fished from about 9:30 to 3:30 and my kid caught 2 walleye- 21" & 25" with a tag. In the past two winters I've made a total of 3 day trips and have a total of 10 walleye from 19-25 inches. I think the numbers may not be a may, but the quality is great. Very similar to the late 90's not as many fish, but great size.
    • hookie
      no live ones that I know of just frozen ones. I heard the run started good than the rain came and dirty the river and moved em back out into the lake.
  • Share & Have Fun