      Fluid forum view allows members only to get right to the meat of this community; the topics. You can toggle between your preferred forum view just below to the left on the main forum entrance. You will see three icons. Try them out and see what you prefer.   Fluid view allows you, if you are a signed up member, to see the newest topic posts in either all forums (select none or all) or in just your favorite forums (select the ones you want to see when you come to Fishing Minnesota). It keeps and in real time with respect to Topic posts and lets YOU SELECT YOUR FAVORITE FORUMS. It can make things fun and easy. This is especially true for less experienced visitors raised on social media. If you, as a members want more specific topics, you can even select a single forum to view. Let us take a look at fluid view in action. We will then break it down and explain how it works in more detail.   The video shows the topic list and the forum filter box. As you can see, it is easy to change the topic list by changing the selected forums. This view replaces the traditional list of categories and forums.   Of course, members only can change the view to better suit your way of browsing.   You will notice a “grid” option. We have moved the grid forum theme setting into the main forum settings. This makes it an option for members only to choose. This screenshot also shows the removal of the forum breadcrumb in fluid view mode. Fluid view remembers your last forum selection so you don’t lose your place when you go back to the listing. The benefit of this feature is easy to see. It removes a potential barrier of entry for members only. It puts the spotlight on topics themselves, and not the hierarchical forum structure. You as a member will enjoy viewing many forums at once and switching between them without leaving the page. We hope that fluid view, the new functionality is an asset that you enjoy .
Sign in to follow this  
eel pout hunter

LP gas and OPD valve problems

Recommended Posts

eel pout hunter    0
eel pout hunter

hey all, in need of some help again.

Just bought my first ice house (used). It has a heater in it, but I'm putting in a stove as well. Its of the Coleman variety with it's own regulator. (kind made to run off of 1lb tanks, but can be used with a bulk cylinder with an adapter). Here's the problem. Every single time, and I mean every time I turn either on, the OPD valve kicks in.

Here's the set up....tank to a 3 ft hose, to a tee...from one leg of the tee is the heater regulator going to the heater. From the other leg is 8ft of 3/8 copper going to the stove regulator. If I take the tee out, and hook up each device directly to the take, they work fine, however with the tee in place the valve kicks in. Not sure why...there are no leaks in the system....any ideas would be greatly appreciated.

pout

Share this post


Link to post
Share on other sites
federline    0
federline

Can you try some different OPD equipped tanks to see if it does it with all OPD valves, or just this one? What year was the tank made in? Some of the first OPD valves didn't flow well at all and were touchy like this.

I would also be suspect of your 3 foot length of hose. If you just use the 3 foot length to one or othe other, does it work OK?

Share this post


Link to post
Share on other sites
tomfromblaine    0
tomfromblaine

Explain what you mean by the opd valve kicks in, my impression was that the opd was a safety device to prevent a over fill/pressure situation. I've heard of opd issues when the outside temp starts to get way down.

Share this post


Link to post
Share on other sites
federline    0
federline

OPD's will kick in in high-flow conditions to prevent things like a ruptured hose from evacuating the entire tank at once. Sometimes, the check-valve kicks in at flow rates that are desired under normal operation.

I've even seen some that, if you turn the wheel on ALL THE WAY, they are much touchier to flow and can check-off. In those cases, don't turn the wheel all the way on.

Share this post


Link to post
Share on other sites
eel pout hunter    0
eel pout hunter

I haven't tried using either device with a 3ft hose....but when I d/c each device from the tee and run it independantly it runs fine. The problem is whenever I put the tee in...with the tee in place neither device works, not even one at a time.

but this is the interesting part. when I d/c the line to reset the valve, I can here gas coming from the line and not the tank (sort of a back pressure, which would explain why the OPD kicks in)

I'm aware of the 1/4 turn trick, don't work either lol

Do you think putting the tee right at the tank would make a difference?

not sure, I've been playing with this for days.

pout

Share this post


Link to post
Share on other sites
eel pout hunter    0
eel pout hunter

OK, here's the update.

Disconnect the whole shootin match...heater works fine. The stove however seems to be the thing that triggers the valve.

It worked at one time. Here's the set up....tank, acme nut, adapter (mpt), 10 ft run of copper 3/8, then 2 3/8 elbows, the reducing to 1/4, to bulk tank adapter, then the regulator.

So here's what I'm thinking, the bulk tank adapter is the wrong kind. By going from 3/8 to 1/4 (the adapter is 1/4 by whatever size those 1lb bottles are) there is too much resistance, thus the back pressure triggering the OPD.

I'm going to call Coleman in the AM. Maybe the regular bulk tank adapter don't work with their stove.

pout

Share this post


Link to post
Share on other sites
Jeremy airjer W    21
Jeremy airjer W

Eelpout, How old is your tank? There should be a four number date stamp on the collar. Some of the older tanks had a considerably lower flow rate than a typical non OPD tank or a newer OPD tank.

The other possibility is that the Excessive Flow Device check valve is tripping. This is an additional safety device designed to limit the flow of propane in the event of a hose bursting. We run into a few of these that are really sensitive and trip when filling the tanks. All we do is shut of the fill valve and then shut off the valve on the tank. Wait for a light clicking noise and start over. We also have alot of people bringing in there full tanks to be filled because they can't get there grill to light. A quick Q&A and we find out they did things in the wrong order and tripped the EFD.

The OPD "Overflow protection device" is nothing more than a "float" that stops the flow of propane "into" the tank when the tank is at its theoretical 80% full. This float/valve has nothing to do with the flow of propane out of the tank.

Share this post


Link to post
Share on other sites
eel pout hunter    0
eel pout hunter

Quote:

Eelpout, How old is your tank? There should be a four number date stamp on the collar. Some of the older tanks had a considerably lower flow rate than a typical non OPD tank or a newer OPD tank.

The other possibility is that the Excessive Flow Device check valve is tripping. This is an additional safety device designed to limit the flow of propane in the event of a hose bursting. We run into a few of these that are really sensitive and trip when filling the tanks. All we do is shut of the fill valve and then shut off the valve on the tank. Wait for a light clicking noise and start over. We also have alot of people bringing in there full tanks to be filled because they can't get there grill to light. A quick Q&A and we find out they did things in the wrong order and tripped the EFD.

The OPD "Overflow protection device" is nothing more than a "float" that stops the flow of propane "into" the tank when the tank is at its theoretical 80% full. This float/valve has nothing to do with the flow of propane out of the tank.


Ok, I figured it was the Flow device portion of the tank. I see a couple of 4 digit numbers on is 43-00.

I spoke with the Coleman people today, all they wanted me to do is buy their hose. I'm off to the local gas company today to talk to them and see what their input is.

I'm starting to think that I've got the wrong style of bulk tank adapter, but I'll keep ya posted.

pout

Share this post


Link to post
Share on other sites
Jeremy airjer W    21
Jeremy airjer W

Your on the right track!

The date stamp is a 2 digit month followed by a 2 digit year. Examples, 12 00 (december of 2000) or 09 94 (september of 1994)

Share this post


Link to post
Share on other sites
eel pout hunter    0
eel pout hunter

OK, here's the final update, the good news is, the problem is solved.

The gas company people were a bit of help. They stated that because of the amount of tubing, the excess flow valve kicks in. They taught me how to open and close the valve like six times in a row to 'purge' the lines. This worked fine on just the stove that I took to them.

They also stated that I could use a POL adapter and that would bypass the excess flow valve. I really wanted an acme nut style fitting so that it would be easy to hook up with cold hands. So they sold me a universal adapter. This was an adapter that was sold after all the grill companies switched to acme nuts, and OPD wasn't a standard. It screws into the POL (inner) thread and has a male acme nut on the other end.

This didn't work however. So basically you need to use a straight POL fitting without the acme nut stuff. Fired it all up tonight and it works fine.

Thanks for your help, just thought that I would post this in case anyone runs into the same problems.

pout

Share this post


Link to post
Share on other sites
Jeremy airjer W    21
Jeremy airjer W

Well I learned something new. I never realized that an empty hose or purging on empty hose would trip EFD, but it makes perfect sense! Everything that I have used has always had the POL ends so I have never run into a problem with the EFD. I'm starting to think that my idea of switching to the ACME connector might not be a good idea!

Share this post


Link to post
Share on other sites
eel pout hunter    0
eel pout hunter

Well then I'm glad I posted the update. I have to go into town today and return the universal adapter ($16). I'm gonna talk to them about the acme nut, it must have something to do with the EFD, reason I say this is because with the universal POL adapter, that is supposed to prevent the EFD from kicking in, not sure why is does.

I guess I should try to find a POL fitting that has a plastic knob on it. They used to make such a critter for gas grills.

pout

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  



  • Posts

    • gimruis
      Here are some of the toads we have been catching on the Rum River this summer.  The biggest has been 19 1/4 inches.
    • gimruis
      I agree with rudrave, a boat will open up a lot more opportunities to fish off shore.  You could get a brand new 16 foot fishing boat with a 25 hp motor and a basic sonar unit with trailer for about $10 grand and that sort of rig would get you on a lot of small to medium-sized lakes in addition to rivers around here.
    • Fish Head
      Enjoy your well-deserved retirement Ace. I'm glad we'll still be hearing from you.          
    • Rick
      The Minnesota Department of Natural Resources has confirmed Hubbard County’s first case of Eurasian watermilfoil, an invasive aquatic plant, in Bad Axe Lake near Emmaville. DNR invasive species specialists confirmed Eurasian watermilfoil around the resort access to the lake. They reported it did not appear to be widespread into other areas of the lake. Eurasian watermilfoil can limit recreational activities on water bodies by forming mats on the water surface, and can alter aquatic ecosystems by displacing native plants. It is typically spread when plant fragments have not been properly cleaned from trailered boats, personal watercraft, docks, boat lifts, anchors or other water-related equipment. Treatment options include selective herbicides and mechanical removal, to minimize the plant’s impact while protecting native aquatic plant species. Treatment is unlikely to eradicate Eurasian watermilfoil from a lake. It may minimize impacts, but rarely prevents broader dispersion within a lake. This new confirmation is a reminder to boaters and anglers to follow Minnesota laws to prevent the spread of aquatic invasive species: Clean aquatic plants and animals from watercraft. Drain all water by removing drain plugs and keep drain plugs out while transporting watercraft. Dispose of unwanted bait in the trash. Some invasive species are small and difficult to see at the access. To remove or kill them, take one or more of the following precautions before moving to another waterbody, especially after leaving infested waters: Spray with high-pressure water. Rinse with very hot water (120 degrees Fahrenheit for at least two minutes or 140 degrees Fahrenheit for at least 10 seconds). Dry for at least five days. Details about Eurasian watermilfoil and other aquatic invasive species are available at mndnr.gov/ais. Discuss below - to view set the hook here.
    • vikingmeatwad
      Did you find any? Let me know where you are located and contact info. Also what size is preferred?
    • BobT
      A popular method that I've seen is to use a slip bobber with minnows, leeches, or crawlers. Four-mile bar seems to be a popular destination but also try working along weed edges. You probably noticed the weedline is about 14' - 15' down so working those edges can be productive. Just my thoughts.
    • BobT
      The purpose for having fuses is to protect the wires and/or downstream devices from over-current situations. When an over-current situation exists the wires can be exposed to higher current than what they are rated to handle and the resulting heat will likely melt the insulation and possibly cause it to burst into flame, which can spread to an on-board fire destroying your boat and everything in it.  A fuse that repeatedly blows when replaced is a good indicator that there is a situation that needs to be resolved. You need to find out what is causing the over-current situation and resolve it. Putting in a higher rated fuse does NOT solve the problem. The wires are rated to a maximum current level and the over-sized fuse will allow excessive current to flow over the wires, which is no better than just getting rid of the fuses. Do not do this.  
    • Capt. Quicksteel
      Have a great retirement Ace. Really glad to hear you'll still stay on the forum!!  
    • SkunkedAgain
      When CigarGuy first showed up on these forums, I stopped by and introduced myself but I think that he was either on his dock or just hopping into the boat. I haven't visually seen him in a few years, but I did see the Mrs. Cigar Guy and another assembling a sitting bench earlier this summer! Some day I'll stop by to share a cocktail.   As for the people boating in close, here are my two Vermilion observations: 1) There are known spots on Vermilion. People go to those whether there are zero boats or ten boats there. If I am on a known spot, I don't get upset when others show up and fish close. If I am working a non-typical spot and others show up because they see you catch a fish, I do get a bit testy as well. 2) Navigation channels tend to hold fish, attracting boats that are fishing and boats that are moving. As a fisherman, I accept that people are going to boat close by in established navigation paths. I do get upset when people go through tight areas on plane or even just below it. I always try to follow a no-wake policy when going through tight areas such as Fectos or others. Our place is in Black Bay and the pinch between Black Bay and the Partridge River typically has boats. I'll come off plane and go nice and slow past boats. Treat others as you want to be treated. Preaching to the choir....I know
    • rundrave
      move back to SD and then buy the boat You dont need to drop $50k on a new boat just to enjoy the water. I have just as much fun fishing about of a super old $500 aluminum boat with a trolling motor as I do fishing in a fully decked out Ranger. There are of course pros and cons to each but you can fish out of both and that's all that matters. And nothing is better than getting away from shore fishing it just opens up so many more opportunities to catch fish.